Tags: POWER SYSTEM STABILITY STUDIES USING MATL, POWER SYSTEM STABILITY STUDIES USING MATLAB ppt, POWER SYSTEM STABILITY STUDIES USING MATLAB pdf, power system stability and control, power system stability analysis, power system stability ppt, power system stability and control by kundur, power system stability and control by prabha kundur, power system stability kimbark, power system stability lecture notes, power system stability and control free ebook, power system stability pdf, power system stability studies,
Ask More Info Of  A Seminar Ask More Info Of A Project Post Reply  Follow us on Twitter
22-03-2010, 02:34 PM
Post: #1
POWER SYSTEM STABILITY STUDIES USING MATLAB full report

.pdf  power system studies using matlab.pdf (Size: 3.66 MB / Downloads: 2199)

Presented By
PRANAMITA BASU
AISWARYA HARICHANDAN
National Institute of Technology Rourkela
Under the guidance of PROF. P.C. PANDA

ABSTRACT
The stability of an interconnected power system is its ability to return to normal or stable operation after having been subjected to some form of disturbance. With interconnected systems continually growing in size and extending over vast geographical regions, it is becoming increasingly more difficult to maintain synchronism between various parts of the power system.
¢ In our project we have studied the various types of stability- steady state stability, transient state stability and the swing equation and its solution using numerical methods using MATLAB and Simulink .
¢ We have presented the solution of swing equation for transient stability analysis using three different methods - Point-by-Point method, Modified Euler method and Runge-Kutta method.
¢ Modern power systems have many interconnected generating stations, each with several generators and many loads. So our study is not limited to one-machine system but we have also studied multi-machine stability.
¢ We study the small-signal performance of a machine connected to a large system through transmission lines. We gradually increase the model detail by accounting for the effects of the dynamics of the field circuit. We have analysed the small-signal performance using eigen value analysis.
¢ Further a more detailed transient stability analysis is done whereby the classical model is slightly improved upon by taking into account the effect of damping towards transient stability response. Characteristics of the various components of a power system during normal operating conditions and during disturbances have been examined, and effects on the overall system performance are analyzed.
INTRODUCTION
Successful operation of a power system depends largely on the engineer's ability to provide reliable and uninterrupted service to the loads. The reliability of the power supply implies much more than merely being available. Ideally, the loads must be fed at constant voltage and frequency at all times. The first requirement of reliable service is to keep the synchronous generators running in parallel and with adequate capacity to meet the load demand. Synchronous machines do not easily fall out of step under normal conditions. If a machine tends to speed up or slow down, synchronizing forces tend to keep it in step. Conditions do arise, however, such as a fault on the network, failure in a piece of equipment, sudden application of a major load such as a steel mill, or loss of a line or generating unit., in which operation is such that the synchronizing forces for one or more machines may not be adequate, and small impacts in the system may cause these machines to lose synchronism.
A second requirement of reliable electrical service is to maintain the integrity of the power network. The high-voltage transmisssion system connects the generating stations and the load centers. Interruptions in this network may hinder the flow of power to the load. This usually requires a study of large geographical areas since almost all power systems are interconnected with neighboring systems.
Random changes in load are taking place at all times, with subsequent adjustments of generation. We may look at any of these as a change from one equilibrium state to another. Synchronism frequently may be lost in that transition period, or growing oscillations may occur over a transmission line, eventually leading to its tripping. These problems must be studied by the power system engineer and fall under the heading "power system stability".
Chapter 2
STUDY OF SWING EQUATION
2.1 STABILITY
The tendency of a power system to develop restoring forces equal to or greater than the disturbing forces to maintain the state of equilibrium is known as "STABILITY'.
The problem of interest is one where a power system operating under a steady load condition is perturbed, causing the readjustment of the voltage angles of the synchronous machines. If such an occurrence creates an unbalance between the system generation and load, it results in the establishment of a new steady-state operating condition, with the subsequent adjustment of the voltage angles. The perturbation could be a major disturbance such as the loss of a generator, a fault or the loss of a line, or a combination of such events. It could also be a small load or random load changes occurring under normal operating conditions. Adjustment to the new operating condition is called the transient period. The system behavior during this time is called the dynamic system performance, which is of concern in defining system stability. The main criterion for stability is that the synchronous machines maintain synchronism at the end of the transient period. So we can say that if the oscillatory response of a power system during the transient period following a disturbance is damped and the system settles in a finite time to a new steady operating condition, we say the system is stable. If the system is not stable, it is considered unstable. This primitive definition of stability requires that the system oscillations be damped. This condition is sometimes called asymptotic stability and means that the system contains inherent forces that tend to reduce oscillations. This is a desirable feature in many systems and is considered necessary for power systems. The definition also excludes continuous oscillation from the family of stable systems, although oscillators are stable in a mathematical sense. The reason is practical since a continually oscillating system would be undesirable for both the supplier and the user of electric power. Hence the definition describes a practical specification for an acceptable operating condition. The stability problem is concerned with the behavior of the synchronous machines after a disturbance. For convenience of analysis, stability problems are generally divided into two major categories-steady state stability and transient state stability and transient state stability.
CONCLUSION AND REFERENCES
8.1 CONCLUSION
Thus we see that a two-machine system can be equivalently reduced to a one machine system connected to infinite bus bar. In case of a large multi-machine system, to limit the computer memory and time requirements, the system is divided into a study subsystem and an external subsystem. The study subsystem is modeled in details whereas approximate modeling is carried out for the rest of the subsystem. The qualitative conclusions regarding system stability drawn from a two-machine or an equivalent one-machine infinite bus system can be easily extended to a multi-machine system.
It can be seen that transient stability is greatly affected by the type and location of a fault so that a power system analyst must at the very outset of a stability study decide on these two factors. For the case of one-machine system connected to infinite bus it can be seen that an increase in the inertia constant M of the machine reduces the angle through which it swings in a given time interval offering a method of improving stability. But this can not be employed in practice because of economic reasons and for the reason of slowing down of the response of the speed-governor loop apart from an excessive rotor weight.
For a given clearing angle, as the maximum power limit of the various power angles is raised, it adds to the transient stability limit of the system. The maximum steady power of a system can be increased by raising the voltage profile of a system and by reducing the transfer reactance. Thus we see that by considering the effect of rotor circuit dynamics we study the model in greater details. We have developed the expressions for the elements of the state matrix as explicit functions of system parameters. In addition to the state-space representation, we also use the block diagram representation to analyse the system stability characteristics.
While this approach is not suited for a detailed study of large systems, it is useful in gaining a physical insight into the effects of field circuit dynamics and in establishing the basis for methods of enhancing stability through excitation control.
We have explored a more detailed model for transient stability analysis taking into account the effect of damping which is clearly visible from the dynamic response of the system. We have included a damping factor in the original swing equation which accounts for the damping taking place at various points within the system.
Our aim should be to improvise methods to increase transient stability. A stage has been reached in technology whereby the methods of improving stability have been pushed to their limits. With the trend to reduce machine inertias there is a constant need to determine availability, feasibility and applicability of new methods for maintaining and improving stability.
8.2 REFERENCES
[I] Nagrath, I.J., and Kothari, D.P., Power System Engineering, New Delhi, Tata McGraw-Hill
Publishing Company Limited, l995.
[2] Saadat, Hadi, Power System Analysis, New Delhi, Tata McGraw-Hill Publishing Company
Limited, 2002.
[3] Wadhwa, C.L., Electrical Power Systems, New Delhi, New Age International publishers, 2005. [4] Yo, Yao-nan, Electrical Power Systems Dynamics, Academic Press, New York, l983. [5] Anderson P.M., Analysis of Faulted Power Systems, IEEE Press, New York,l973. [6] ] Kundur Prabha, Power System Stability and Control, Tata McGraw-Hill, 2007.
[7] W.D. Stevenson, Elements of Power System Analysis, 3rd Edition, McGrawHill,l975 [8] R.T. Byerly and E.W.Kimbark, Stability of Large Electric Power Systems, IEEE Press,l974 [9] E.R. Laithwaite and L.L.Freris, Electric Energy: Its Generation, Transmission and Use, McGraw-Hill (UK), l980
[l0] B.Stott, "Power System Dynamic Response Calculations", Proc IEEE, Vol.67, pp.2l0-24l, February l979
[II] N.Kakimoto, Y.Ohsawa, and M. Hayashi, "Transient Stability Analysis of Electric Power
System Via Lure, Type Lyapunov Functions, Parts I and II," Trans. IEE of Japan, Vol.98, No.5l6,
May/June l978
[l2] A.A. Fouad and S.E. Stanton, "Transient Stability of Multi machine Power System, Parts I and II," IEEE Trans., Vol. PAS-l00, pp. 3408-3424, July l98l

Please Use Search http://www.seminarprojects.com/search.php wisely To Get More Information About A Seminar Or Project Topic
12-09-2010, 08:51 AM
Post: #2
RE: POWER SYSTEM STABILITY STUDIES USING MATLAB full report
can you give me the whole project report of transient stability analysis of single machine system by rungekutta method in matlab

Please Use Search http://www.seminarprojects.com/search.php wisely To Get More Information About A Seminar Or Project Topic
07-10-2010, 11:32 AM
Post: #3
RE: POWER SYSTEM STABILITY STUDIES USING MATLAB full report
This article is presented by:
Satish J Ranade
Classical Analysis
Equal Area Criterion
Power System Dynamics and Transients
A generator connected to an infinite bus through a line. Initially Pm=Pe
Stability is governed by the Swing Equation
d2δ/dt2 = (πf/H) (Pm-Pe)

dδ /dt = ω-ωsyn

Swing Equation


Power Angle
Equation

Pe = E’ V sin (δ) /(X+XL)

First swing stability-Equal Area Criterion
Stable Equilibrium—small increase in mechanical power


At D ω is decreasing but > 0
δ increases further say to point E
By now suppose ω is back to zero and decreasing
Thus ω becomes < 0 as the generator continues to slow
Since ω<0 δ decreases towards B First swing stable!


For more information about this article,please follow the link:
http://www.ece.nmsu.edu/~sranade/EE532_06_8.ppt

Please Use Search http://www.seminarprojects.com/search.php wisely To Get More Information About A Seminar Or Project Topic
Rating POWER SYSTEM STABILITY STUDIES USING MATLAB full report Options
Share POWER SYSTEM STABILITY STUDIES USING MATLAB full report To Your Friends :- Seminar Topics Bookmark
Post Reply 

Marked Categories : power system control stability anderson fortran programm, point by point solution of swing equation, matlab linear programming ieee 5 bus and 30 bus, swing equation matlab stability, powerflow fortran, abstract on power systam stability full matlab scfcls, abstract on power systam stability full matlab, power systam stability full matlab, ppt single machine connected to infinite bus, transient stability analysis using matlab, power system stability and control kundur pdf, download matlab power system projects, multimachine system matlab code, matlab simulink on power application, multimachine system stability matlab program, power system stability ppt,

[-]
Quick Reply
Message
Type your reply to this message here.


Image Verification
Image Verification
(case insensitive)
Please enter the text within the image on the left in to the text box below. This process is used to prevent automated posts.

Possibly Related Threads...
Thread: Author Replies: Views: Last Post
  PRODUCTION PLANNING AND CONTROL full report seminar ideas 1 556 Yesterday 10:41 PM
Last Post: Guest
  green power storage swetha reddy.3132 7 4,751 Yesterday 05:49 PM
Last Post: Guest
  PRE PAID ENERGY METER full report seminar girl 3 2,136 Yesterday 02:10 PM
Last Post: mattmro
  iris recognition system project mehabub 9 3,320 Yesterday 09:26 AM
Last Post: study tips
Star Mechanical seminar (Full report + ppt slides) mechstar48 26 33,230 23-05-2013 09:35 AM
Last Post: study tips
Thumbs Up atm database system abstract Guest 4 977 23-05-2013 09:33 AM
Last Post: study tips
Wink load sensing hydraulic system Guest 1 40 23-05-2013 09:29 AM
Last Post: study tips
  UNIVERSITY MANAGEMENT SYSTEM full report project topics 20 14,275 23-05-2013 09:26 AM
Last Post: study tips
  vb net source code for institute management system Guest 4 2,244 23-05-2013 09:22 AM
Last Post: study tips
  Modeling and Simulation Five Level Inverter based UPFC System pdf study tips 0 56 22-05-2013 04:59 PM
Last Post: study tips
This Page May Contain What is POWER SYSTEM STABILITY STUDIES USING MATLAB full report And Latest Information/News About POWER SYSTEM STABILITY STUDIES USING MATLAB full report,If Not ...Use Search to get more info about POWER SYSTEM STABILITY STUDIES USING MATLAB full report Or Ask Here

Options: